Backup Power

I guess you don't relize what you need until you don't have it. My question is, what do you do for your backup power? What would you consider "essential" equipment to keep on a battery backup? Does anyone have any recomendations as to what APC BackUPS to use?
__________________

__________________
Ximat is offline   Reply With Quote
Old 03-24-2005, 10:36 PM   #2
Aquarium Advice FINatic
 
Join Date: May 2004
Location: Richmond, Va
Posts: 804
A UPS can be used to keep a ph and heater running for a while if you lose power when not at home. For longer outtages I keep a 400w power inverter handy. I don't use a UPS for my tank so I don't have any recommendations. It's one of those things you hope you never need.
__________________

__________________
46g SW, 65 lbs Fiji LR, 4" Aragamax DSB, Coralife 2X96w CF, CPR Bakpak II, CPR Aquafuge 12 w/ 2x9 Coralife Mini Aqualight, 4 Maxijet 600's, PCI 200W Titanium Heater, 2 Blue Green Chromis, 1 Gold Bar Maroon Clown, 1 Purple-Stripe Dottyback, Finger Leather, Trumpets, Rose Coral Open-Brain, Pagoda Cup, Xenia, Star Polyps, Yellow Polyps, Various Mushrooms, Toadstool Leather, 12 Astraea, 10 Nassarius, 4 Bumble Bee, 6 Cerith Snails, 12 Red Tip Hermits.
phases99 is offline   Reply With Quote
Old 03-24-2005, 11:26 PM   #3
Aquarium Advice Freak
 
Join Date: Jan 2005
Location: Arkansas, USA
Posts: 278
Send a message via AIM to Ximat
I was thinking about a UPS to power 1 of my two Filters, both heaters and one powerhead. Shouldn't be too much current draw. Tonight we lost power for a couple hours, but that was because someone ran over a pole. Not a frequent thing, but i hate to be left in the dark, for lack of better words.
__________________
Ximat is offline   Reply With Quote
Old 03-24-2005, 11:33 PM   #4
Aquarium Advice Activist
 
Join Date: Sep 2004
Location: Illinios, USA
Posts: 137
You will not power a heater for any great length of time off a UPS current draw is too much-Anne
you can run the filter tho
__________________
There can never be to many bichir creature keepers
beblondie is offline   Reply With Quote
Old 03-24-2005, 11:46 PM   #5
Aquarium Advice Freak
 
Join Date: Jan 2005
Location: Arkansas, USA
Posts: 278
Send a message via AIM to Ximat
The heaters really draw that much power? Im know nothing about power so i don't know. I figured they didn't have too much draw.
__________________
Ximat is offline   Reply With Quote
Old 03-24-2005, 11:51 PM   #6
Aquarium Advice Activist
 
Join Date: Sep 2004
Location: Illinios, USA
Posts: 137
yup they do remember they work by heating high resistence wire they are probably the most expensive thing to operate in your aquarium.-Anne
__________________
There can never be to many bichir creature keepers
beblondie is offline   Reply With Quote
Old 03-25-2005, 12:56 AM   #7
Aquarium Advice FINatic
 
Join Date: Oct 2004
Location: Tulsa
Posts: 562
I have a 1800 genny ready to go at a moments notice along with a 5000 if needed. It scared the crap out of me to hink about power outages here in tornado alley, we have had two god storms in the last two days allready with a few tornadoes fairly close. I watched a transformer blow up down the road the other night and the houses across the street lost power for most of the night. Sceeeery,lol
__________________
150 rr Oceanic, 300 pound lr,250 pounds ls, lps's, polyp's,soft corals, sps's,
Thumper is offline   Reply With Quote
Old 03-25-2005, 06:03 AM   #8
Smo
Aquarium Advice Regular
 
Join Date: Mar 2005
Location: Arizona
Posts: 92
I sure hate to rain on your parade, but..................
APC's Back-UPS line is designed for use with Computer-type loads only. They are not designed to be used with motor loads such as fish filters, air conditioning units, space heaters, vacuum cleaners or any other machinery.

One potential issue is the inrush current draw for a motor. It can easily overload a Back-Ups UPS model. Secondly, these models of UPSs output a Stepped-Approximated sine wave when on battery. This waveshape, while ideal for computer-type equipment, is not particularly compatible with most motor loads. The result may be that motor runs very slowly, erratically, or not at all when the UPS is on battery.

To protect this type of equipment, APC recommends first determining the appropriate size UPS for the motor load in question. Ensure that the Volt Amp rating of the UPS is sufficient to handle the start-up inrush current draw of the motor. Secondly, select a UPS which outputs a Pure Sine Wave when on battery, such as a Smart-UPS (minimum of a SU700), Matrix-UPS, or Symmetra Power Array.


This info gleaned from the APC website!
__________________
29gal BB | 42+ lbs LR | 143watts PC | Asst. Leathers, Frogspawn, Hammer, XLG Open Brain, Zoanthids, Mushrooms, Diploastrea heliopora | Blue Mandarin | Atrosalarias Fuscus | Pair Captive Bred Ocellaris Clowns | Peppermint Shrimp | 6 Astrea's |
Smo is offline   Reply With Quote
Old 03-25-2005, 06:47 AM   #9
Aquarium Advice Activist
 
Join Date: Sep 2004
Location: Illinios, USA
Posts: 137
And mine was from expirence with eheim canister filter.''They are not designed to be used with motor loads such as fish filters, air conditioning units, space heaters, vacuum cleaners or any other machinery." Thats a legal disclamer,Just because it wasn't designed for a purpose doesn't mean it will not work.I did forget 1 important thing your filter needs to be self priming.Since it couldshut off and lose its prime before the battery takes over-Anne
__________________
There can never be to many bichir creature keepers
beblondie is offline   Reply With Quote
Old 03-25-2005, 08:11 AM   #10
Aquarium Advice Freak
 
Join Date: Jan 2005
Location: Arkansas, USA
Posts: 278
Send a message via AIM to Ximat
So since you rained on my parade, any recomendations? Im not wanting to drop a couple grand on a generator though.
__________________

__________________
Ximat is offline   Reply With Quote
Reply

Please support our sponsors and let them know you heard about them on AquariumAdvice.com

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
battery backup zilla870 Freshwater & Brackish - General Discussion 11 04-24-2005 02:05 AM
Backup plans for power failure? grimlock3000 Saltwater Reef Aquaria 9 02-11-2005 08:24 PM
Power backup cginflorida General Hardware/Equipment Discussion 6 06-07-2004 08:19 PM
I need fish backup! lyquidphyre Aquaria Off-Topic 15 05-25-2004 06:04 PM







» Photo Contest Winners








Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -4. The time now is 09:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.